NEC 110.26(C)(2) clearance requirement

Status
Not open for further replies.

anbm

Senior Member
See attached picture, to meet NEC 110.26(C)(2) and exhibit 110.20, should a new door be added to North East the room
enough?
 

Attachments

  • elec room.PNG
    elec room.PNG
    97.2 KB · Views: 26

gh0st

Member
Location
California
Occupation
Designer
If you have double the clearances maintained a second door is not required. Even so, adding the door would probably be recommended. Hate to be trapped back there during an arcing event.
 