Re: NEC 2005 Art. 250.52(A)(3) Concrete-Encased Electrode
Thank you to all contributors for their postings. Additional information for the usage of the posted ohmic values in Bryan's posting:
"In 1942, H.G. Ufer performed an 18 year study on the resistance of concrete-encased electrodes. At the end of the study in 1960, the average of 24 installations was 3.57 ohms, none every exceeding 4.8 ohms over the 18 years. The best reading was 2.1 ohms.
The study was performed in two soil types. One in dry sand and gravel, the other in moist clay, shale, gumbo, and loam.
Now for the important question. So what? What is the application you are installing that the ground resistance is so important??
is as follows:
///The project location and soil composition are known. The ground resistance is specified in the Specifications as: "Ohmic resistance between the equipment and the earth shall not exceed ten (10) ohms." The Project includes a large underground "Rebar Concrete Box" that will house Industrial/Commercial Rooms, and two light rail tracks (several hundred yard long). Since the rebars meet NEC "Concrete-Encased Electrode" requirements, grounding connection access to concrete rebars (Concrete-Encased Electrodes) have to be depicted on Project Drawings in terms of number of locations that would meet the specified ohmic value of 10 ohms or less. This is the normal and prudent electrical engineering, design and construction aspect.\\\