NEC 2005 Garage Receptacles?

Status
Not open for further replies.

The Iceman

Senior Member
Location
Florida
On my last exam it showed a picture of a garage with three duplex receptacles, one on each wall about 18" off the floor. One of the duplex receptacle had a freezer plugged into it. The question was how many receptacles need to be GFCI?
Reading 210.8 (A) (2) Ex. 2 I would guess 5 receptacles need to be GFCI. What I'm not 100% sure about is are they counting each duplex receptacle as 1 or 2 receptacles? This exam was on the 2005 NEC.
 
The Iceman said:
On my last exam it showed a picture of a garage with three duplex receptacles, one on each wall about 18" off the floor. One of the duplex receptacle had a freezer plugged into it. The question was how many receptacles need to be GFCI?
Reading 210.8 (A) (2) Ex. 2 I would guess 5 receptacles need to be GFCI. What I'm not 100% sure about is are they counting each duplex receptacle as 1 or 2 receptacles? This exam was on the 2005 NEC.

The duplex recep. is one device. The recep. for the freezer in 05 was exempt from the GFCI requirements in a garage. In 2008 there is no exception.
 
Dennis Alwon said:
The duplex recep. is one device. The recep. for the freezer in 05 was exempt from the GFCI requirements in a garage. In 2008 there is no exception.

But the receptacle for the freezer is a duplex. I think one of those receptacles on that yoke would need to be GFCI.:confused:
 
The Iceman said:
On my last exam it showed a picture of a garage with three duplex receptacles, one on each wall about 18" off the floor. One of the duplex receptacle had a freezer plugged into it. The question was how many receptacles need to be GFCI?
Reading 210.8 (A) (2) Ex. 2 I would guess 5 receptacles need to be GFCI. What I'm not 100% sure about is are they counting each duplex receptacle as 1 or 2 receptacles? This exam was on the 2005 NEC.


In regards to test questions, each duplex receptacle will count as 2 receptacles.
For your test question, there are 6 receptacles.
There is 1 receptacle for the dedicated equipment, so 5 receptacles would require GFCI protection.
 
I'm curious to know the answers.
Example: Lets say we had two duplex receptacles mounted 42 inches off the floor in a garage, and I asked how many receptacles needed to be GFCI protected:
A. 2
B. 1
C. None

If you look at the example question I asked. Did you see any answers that said four (4). Then the answer is two.
 
Thanks for the quick response. After reading over 210.8 and the definition for receptacle, I agree with 5 being the answer. You guys are very helpful, sometimes I need a little verification. More previous exam question coming soon.:)
 
The Iceman said:
But the receptacle for the freezer is a duplex. I think one of those receptacles on that yoke would need to be GFCI.:confused:
See the 2005 NEC Exception No. 2 to (2): A single receptacle or a duplex receptacle for two appliances located within dedicated space for each appliance that, in normal use, is not easily moved from one place to another and that is cord-and-plug connected in accordance with 400.7 (A)6; (A)7 and (A)8


The 2008 deleted the requirement saying:All 15- and 20-ampere receptacles in garages and accessory buildings at dwelling units must have GFCI protection for personnel. The two exceptions to this requirement were deleted in the 2008 Code
 
480sparky said:
What does 18" or 42" AFF have to do with it?

What are you talking about!?

I posted an example (meaning: It's made up) question to show that some questions have common sense answers.
 
resistance said:
What are you talking about!?

I posted an example (meaning: It's made up) question to show that some questions have common sense answers.

The Iceman said:
On my last exam it showed a picture of a garage with three duplex receptacles, one on each wall about 18" off the floor. One of the duplex receptacle had a freezer plugged into it. The question was how many receptacles need to be GFCI?
Reading 210.8 (A) (2) Ex. 2 I would guess 5 receptacles need to be GFCI. What I'm not 100% sure about is are they counting each duplex receptacle as 1 or 2 receptacles? This exam was on the 2005 NEC.

resistance said:
I'm curious to know the answers.
Example: Lets say we had two duplex receptacles mounted 42 inches off the floor in a garage, and I asked how many receptacles needed to be GFCI protected:
A. 2
B. 1
C. None

If you look at the example question I asked. Did you see any answers that said four (4). Then the answer is two.

I'm saying the height of the receps has no bearing on whether they are required to be GFCI protected.
 
benaround said:
What if they were 12' aff for garage door opener?

Then in "05" they would be "not readily accessible" and not need to be GFCI protected, in "08" they would need to be GFCI protected. And if you are a jerk you could put a GFCI receptacle in the ceiling so the HO has to climb up there to reset it if it trips.:grin:
 
benaround said:
What if they were 12' aff for garage door opener?


If it's a single receptacle installed specifically for the operator, then no, it doesn't have to be GFId. 210.8(A)(2) Exc. 1. But there's no hieghts mentioned in that article for general-purpose receps. So their being 12" or 44" or 68" or 15000" off the floor makes no difference.
 
Hey I saw this on the Master exam and the Question had that pic like stated but it said how many OUTLETS require GFI protection DISREGARDING EXCEPTIONS. The answers were A.2,B.3,C.4& D.5. So I came up with C.4 being that there are 4 outlets that require GFI protection. Anybody think of this also??
 