What does it mean 25% of the largest motor(see 430.24)?
Line A Neutral Line B
3 3 2
Line A Neutral Line B
3 3 2
They have determined that the voltage requirements in this example is 1- phase 240,1-phase 120 and 1-phase 115,,and resultant amps are listed for each load ,they are loaded on the phase conductors as shown for the best balance on both line and neutral.Total this up and then multiply the largest load by 1.25% and add it to your total,use this largest line amp total column to size your feeder.If you can determine that something cannot run while certain other units are running then you can reduce the amp total by that units load.You can down size the neutral if you want or go full size,depending on the economics .
dick
But did you notice that only two of the three wires would have 25% added to them if only the largest amperage was used, rather than the largest on each conductor. In the example, they added 25% to all three wires. That means they added the largest motor current on each, which is comprised of two separate motors