I understand how to size per NEC 690, but I have some questions regarding the 310 tables.
First question:
In trying to size 3 PV DC feeders (6 conductors) run in cable tray, which table is applicable? All tables I would normally use in NEC 2008 have been changed and it now seems the tables are limited to 3 current carrying conductors.
Second question:
The cable tray feeders transition to underground conduit. All solar design guides I have found instruct me to use tables 310.15. My question is should I be using the Annex B tables and interpolation because the conduits are run underground? Generally solar is not "on" all the time and I don't know if this would affect the "load factor," but I know that the thermal resistivity value (rho) is going to affect the ampacity.
Currently I am modeling based off Table 310.15(B)(16) and verifying thermal requirements with an ETAP simulation.
There are whole new issues opened up when deciding how to meet 392 cable tray ampacity requirements but one problem at a time
I am fairly new to this and would much appreciate some direction.
First question:
Second question: