NEC 2011, Table 770.154(a) Optical Fiber Cables & Raceways

Status
Not open for further replies.

Garry99

New member
Location
Chesapeake VA
I am a little confused about the very first row of the table. " In fabricated ducts". The table indicates N for everything except OFNP & OFCP.
It appears that the table is allowing installation of OFNP & OFCP in fabricated ducts without a metal raceway, however the column to the left
states " In fabricated ducts as described in 300.22(B)" that requires a metal raceway for everything. If this is the case, then why is the first row separated from the second row "In metal raceway that complies with 300.22(B)?
 
Status
Not open for further replies.
Top