codequestion
Banned
- Location
- MD, USA
Attached Trough pdf. Can you bond the 14x14 trough as shown on the attached pdf to main service disconnect and CT cabinets and panels per NEC 2014 Article 250.118(13)?
They are supposed to be electrically continuous anyway.Attached Trough pdf. Can you bond the 14x14 trough as shown on the attached pdf to main service disconnect and CT cabinets and panels per NEC 2014 Article 250.118(13)?
Same thing that happens if you don't have metal raceways or enclosures and an EGC fails for some reason.Are you using the raceway as your equipment ground conductor? Seems a bit odd not to carry a ground conductor from your 1600A service. What happens when someone forgets a locknut.