NEC 2014 Article 250.118(13)

Status
Not open for further replies.

codequestion

Banned
Location
MD, USA
Attached Trough pdf. Can you bond the 14x14 trough as shown on the attached pdf to main service disconnect and CT cabinets and panels per NEC 2014 Article 250.118(13)?
 

Attachments

  • Trough.pdf
    105.5 KB · Views: 0
It is on the load side of the service disconnect, so the code will permit that installation. Not sure I would do it that way, but the code says it is ok.
 
Attached Trough pdf. Can you bond the 14x14 trough as shown on the attached pdf to main service disconnect and CT cabinets and panels per NEC 2014 Article 250.118(13)?

Are you using the raceway as your equipment ground conductor? Seems a bit odd not to carry a ground conductor from your 1600A service. What happens when someone forgets a locknut.
 
Attached Trough pdf. Can you bond the 14x14 trough as shown on the attached pdf to main service disconnect and CT cabinets and panels per NEC 2014 Article 250.118(13)?
They are supposed to be electrically continuous anyway.

Are you using the raceway as your equipment ground conductor? Seems a bit odd not to carry a ground conductor from your 1600A service. What happens when someone forgets a locknut.
Same thing that happens if you don't have metal raceways or enclosures and an EGC fails for some reason.
 