I have conduit from dispenser going underground underneath building and coming up in electric room inside building. Seals as required by NEC 2014 Article 514 for conduit going thru class 1 are installed when come up in electric room. Does Nec 2014 req any min or max height once conduit enter the room for seal installation?

Sent from my SM-G935U using Tapatalk
 
Yes, but it's pretty broad. Just within 10 feet of the point of emergence from grade. See Section 514.8
 