Nec 2014 grouping

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows Panel A, Panel B, Panel C, Panel D which have main breaker and are service disconnects.

Top part shows layout location and bottom part is the single line. Panels A to C are outside building wall attached but Panel D is inside building wall back to back of Panel B and Panel C.

The question is would Panels A to Panel D be considered grouped per code?
7c927ca2b274d255098acdb2cc517348.jpg


Sent from my SM-G935U using Tapatalk
 
My answer: A, B, and C are grouped. D is not grouped with the others. I would call this a violation.
 