hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Attached sketch shows Side View and Front View. Structure is built around panelboards which supports two transformers as shown on the sketch.

I looked at 110.26(E)(1)(a) but it’s confusing structure is for electrical equipment which supports the transformer but not sure if it would be allowed or have to have certain height. The height from top of panelboards to structure labeled A in the sketch should it be 6 feet or can it be less or more than 6 feet?
 

Attachments

  • 2ED8A0B7-1FC8-4C80-85F3-BB8A37293F2A.jpeg
    2ED8A0B7-1FC8-4C80-85F3-BB8A37293F2A.jpeg
    74.6 KB · Views: 17

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
agree.. your sketch does not give that dimension but as long a the transformer & support structure allows the 6'5 clearance from the floor and the space above the panel equal to the depth of the panel is clear (transformers set off from wall as shown), it should be o.k.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
agree.. your sketch does not give that dimension but as long a the transformer & support structure allows the 6'5 clearance from the floor and the space above the panel equal to the depth of the panel is clear (transformers set off from wall as shown), it should be o.k.

What if the transformer was not set off from wall? What if transformer touches the wall like attached sketch? Then what?
 

Attachments

  • D57FABC5-9D4E-4205-B342-760454E1F5EC.jpeg
    D57FABC5-9D4E-4205-B342-760454E1F5EC.jpeg
    64.5 KB · Views: 10

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
below is more accurate picture of what it looks like. I guess the transformer needs to be moved to the left a little in the red mark region it would obstruct the space above the panel equal to the depth of the panel?

View attachment 2553083
 
Last edited:

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
agree.. your sketch does not give that dimension but as long a the transformer & support structure allows the 6'5 clearance from the floor and the space above the panel equal to the depth of the panel is clear (transformers set off from wall as shown), it should be o.k.

Why can’t transformer be installed not set off from the wall shown post #6 it is an electrical install and allowed by 110.26(E)(1)(a) no?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
The reason for the 6 ft clear space over the panels is to allow additional conduits to be installed at later dates.
The transformer must be set out at least the depth of the cabinet to allow for this.
 