I have outside feeder going into building. Right where they come up the designer is placing a new MLO panelboard with provision of 12 spaces. Out of those 12 space 2 will be used as breakers.
NEC 2014 Section 225.33(A) says six switches or six breakers but the designer has provision for 12 spaces so anyone can put more than 12 breakers. I advise to put either main breaker panelboard or six breakers panelboard but he says it’s not in code violation at present since he is placing two breakers. Says someone does it in future more than six then they are at fault not him.
My biggest concern is if you put new panelboard 12 spaces that means it is ok put breakers in future as well so designer can get into fault. Someone can place more than six breakers.
Not sure what to do. Is the designer correct or I am correct? Does anyone have any opinion should panelboard be MLO 12 spaces or panelboard have main breaker and 12 spaces?
NEC 2014 Section 225.33(A) says six switches or six breakers but the designer has provision for 12 spaces so anyone can put more than 12 breakers. I advise to put either main breaker panelboard or six breakers panelboard but he says it’s not in code violation at present since he is placing two breakers. Says someone does it in future more than six then they are at fault not him.
My biggest concern is if you put new panelboard 12 spaces that means it is ok put breakers in future as well so designer can get into fault. Someone can place more than six breakers.
Not sure what to do. Is the designer correct or I am correct? Does anyone have any opinion should panelboard be MLO 12 spaces or panelboard have main breaker and 12 spaces?