FYI- just got off the phone with an individual in the know. Wanted to address Dennis question about the 6' language. While keiths PC was rejected it made total sense. By moving that connecting edge they helped the measurement but leaving the 6' language created a situation where no receptacle could be needed to serve on the peninsular countertop...which was less safe than in the previous edition. Now in the IAEI AOC it says " The final language at 210.52 (C)(3) allows a receptacle outlet at the connecting wall (which serves the base countertop) to serve the peninsular countertop as well"
They also go on to say " This 6' restriction was removed at the 2017 NEC Second Draft stage allowing the wall receptacle outlet to serve the base countertop as well as all the peninsular countertop, regardless of the length of the peninsular countertop."
That is also what was conveyed to me by a panel member...but as you can see a member I talked to today did not agree....BUT again I like David's way of thinking...I can only bring you what was expressed to me...and sorry for the multiple posts....I kinda got into this one as I like these kinds of conversations..sorry.
Comments based on the 2017 National Electrical Code.
They also go on to say " This 6' restriction was removed at the 2017 NEC Second Draft stage allowing the wall receptacle outlet to serve the base countertop as well as all the peninsular countertop, regardless of the length of the peninsular countertop."
That is also what was conveyed to me by a panel member...but as you can see a member I talked to today did not agree....BUT again I like David's way of thinking...I can only bring you what was expressed to me...and sorry for the multiple posts....I kinda got into this one as I like these kinds of conversations..sorry.
Comments based on the 2017 National Electrical Code.