310.3 Conductors.
(A) Minimum Size of Conductors.
The minimum size of conductors for voltage ratings up to and including 2000 volts shall be 14 AWG copper or 12 AWG aluminum or copper-clad aluminum, except as permitted elsewhere in this Code.
I have my 2023 NFPA70 ,
310.3(A) was not modified. However; 210.18 Rating has added 10ampere branch circuits.
210.18 Rating.
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 10, 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
According to Table 210.24(1), we must use 14AWG copper or 12AWG aluminum/ copper-clad.
This is the same conductor size requirement for 15 ampere circuits.
SO WHAT IS THE POINT OF USING A 10 AMPERE RATED BRANCH CIRCUIT IF WE HAVE TO USE THE SAME SIZE CONDUCTORS FOR 15 AMPERE BRANCH CIRCUITS. AM I MISSING SOMETHING HERE? WAS THERE A MISTAKE IN THE 2023 NFPA70? WHAT DOES IT PROFIT A MAN TO GAIN THE ABILITY TO USE A 10A OCPD, JUST TO LOSE HIS CONDUCTORS??
(A) Minimum Size of Conductors.
The minimum size of conductors for voltage ratings up to and including 2000 volts shall be 14 AWG copper or 12 AWG aluminum or copper-clad aluminum, except as permitted elsewhere in this Code.
I have my 2023 NFPA70 ,
310.3(A) was not modified. However; 210.18 Rating has added 10ampere branch circuits.
210.18 Rating.
Branch circuits recognized by this article shall be rated in accordance with the maximum permitted ampere rating or setting of the overcurrent device. The rating for other than individual branch circuits shall be 10, 15, 20, 30, 40, and 50 amperes. Where conductors of higher ampacity are used for any reason, the ampere rating or setting of the specified overcurrent device shall determine the circuit rating.
According to Table 210.24(1), we must use 14AWG copper or 12AWG aluminum/ copper-clad.
This is the same conductor size requirement for 15 ampere circuits.
SO WHAT IS THE POINT OF USING A 10 AMPERE RATED BRANCH CIRCUIT IF WE HAVE TO USE THE SAME SIZE CONDUCTORS FOR 15 AMPERE BRANCH CIRCUITS. AM I MISSING SOMETHING HERE? WAS THERE A MISTAKE IN THE 2023 NFPA70? WHAT DOES IT PROFIT A MAN TO GAIN THE ABILITY TO USE A 10A OCPD, JUST TO LOSE HIS CONDUCTORS??
Circuit Rating | 10 A | 15 A | 20 A | 30 A | 40 A | 50 A |
---|---|---|---|---|---|---|
Conductors (min. size): | ||||||
Circuit wires | 14 | 14 | 12 | 10 | 8 | 6 |
Taps | 14 | 14 | 14 | 14 | 12 | 12 |
Fixture wires and cords | See 240.5. | |||||
Overcurrent Protection | 10 A | 15 A | 20 A | 30 A |