MtnTen79
Member
- Location
- Philadelphia, PA
- Occupation
- Electrical Designer
A 5.2kVA UPS is being installed to serve lab equipment. The manufacturer has stated that the unit comes with a 30A cord and plug that will require an L6-30R receptacle and should be fed from a 40A two-pole circuit breaker (208V, single-phase).
NEC 210.21(B)(1) states "A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit."
The manufacturer is calling for a 40A circuit breaker to feed a 30A receptacle, which appears to be in violation of NEC 210.21(B)(1).
Is anyone aware of any exceptions that may apply to a UPS, or similar equipment that could possibly allow what the manufacturer is suggesting?
Thank you for any help or explanation you can provide.
NEC 210.21(B)(1) states "A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit."
The manufacturer is calling for a 40A circuit breaker to feed a 30A receptacle, which appears to be in violation of NEC 210.21(B)(1).
Is anyone aware of any exceptions that may apply to a UPS, or similar equipment that could possibly allow what the manufacturer is suggesting?
Thank you for any help or explanation you can provide.