NEC 210.21(B)(1) - 40A CB feeding 30A Receptacle

Status
Not open for further replies.

MtnTen79

Member
Location
Philadelphia, PA
Occupation
Electrical Designer
A 5.2kVA UPS is being installed to serve lab equipment. The manufacturer has stated that the unit comes with a 30A cord and plug that will require an L6-30R receptacle and should be fed from a 40A two-pole circuit breaker (208V, single-phase).

NEC 210.21(B)(1) states "A single receptacle installed on an individual branch circuit shall have an ampere rating not less than that of the branch circuit."

The manufacturer is calling for a 40A circuit breaker to feed a 30A receptacle, which appears to be in violation of NEC 210.21(B)(1).

Is anyone aware of any exceptions that may apply to a UPS, or similar equipment that could possibly allow what the manufacturer is suggesting?

Thank you for any help or explanation you can provide.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
Welcome to the forum.

You're correct. The UPS manufacturer's instructions do not supersede NEC requirements.

They need to come up with a compliant solution, like a smaller breaker or a larger receptacle.
 

tom baker

First Chief Moderator
Staff member
Welcome to the forum.

You're correct. The UPS manufacturer's instructions do not supersede NEC requirements.

They need to come up with a compliant solution, like a smaller breaker or a larger receptacle.
They may want the larger OCPD for UPS inrush on startup. It’s a mfg issue.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
As an installer if it comes with a 30 amp plug it gets a 30 amp receptacle and a 30 amp OCPD. If it doesn't work that's the manufacturers problem.
 