Hi everyone, first post here. I'm not an electrical engineer/electrician and I'm relatively new to this field, so please bear with me if some of my terminology or foundational knowledge is lacking.
I'm working on designing some panels for a project and am at the stage where I need to size the circuit breakers. I have a panel with a feeder going to several branch circuits, for which the circuit breaker ratings have been selected. When I looked into sizing the circuit breaker for the feeder, I found NEC and UL 508A information that appears to be in conflict, so I'm hoping someone can help point out what I'm missing here.
Excerpt from NEC 215.3 - Overcurrent Protection (2023):
"Where a feeder supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load."
UL 508A 32.3.1 - Sizing of overcurrent protection (of feeder) (2022):
"The size of the overcurrent protection shall not exceed the ampere value determined from (a) and (b), whichever is larger:
a) The rating of the largest branch circuit protective device in the circuit plus 125 percent of all heater loads plus the full-load currents of all other motors or other loads in the group that could be in operation at the same time; or
b) The ampacity of the conductors or bus bars on the load side of the overcurrent device."
I've tested some scenarios and the result you get from UL 508A 32.3.1 is lower than the result you get from NEC 215.3 in some cases, particularly if using a conductor with the lowest ampacity possible that can handle the load. So if I calculate, for example, 30 A from UL 508A 32.3.1 and 34.5 A from NEC 215.3, I have a contradiction: UL 508A is telling me to not exceed 30A, while NEC is telling me not to go lower than 34.5 A, so one method results in a 30 A circuit breaker and the other results in a 40 A circuit breaker.
Am I missing something here? I found a question similar to this on this forum a couple years back, but the answers didn't provide any clarification for me. Any help would be greatly appreciated, thanks for bearing with me as I try to understand a completely new field of knowledge.
I'm working on designing some panels for a project and am at the stage where I need to size the circuit breakers. I have a panel with a feeder going to several branch circuits, for which the circuit breaker ratings have been selected. When I looked into sizing the circuit breaker for the feeder, I found NEC and UL 508A information that appears to be in conflict, so I'm hoping someone can help point out what I'm missing here.
Excerpt from NEC 215.3 - Overcurrent Protection (2023):
"Where a feeder supplies continuous loads or any combination of continuous and noncontinuous loads, the rating of the overcurrent device shall not be less than the noncontinuous load plus 125 percent of the continuous load."
UL 508A 32.3.1 - Sizing of overcurrent protection (of feeder) (2022):
"The size of the overcurrent protection shall not exceed the ampere value determined from (a) and (b), whichever is larger:
a) The rating of the largest branch circuit protective device in the circuit plus 125 percent of all heater loads plus the full-load currents of all other motors or other loads in the group that could be in operation at the same time; or
b) The ampacity of the conductors or bus bars on the load side of the overcurrent device."
I've tested some scenarios and the result you get from UL 508A 32.3.1 is lower than the result you get from NEC 215.3 in some cases, particularly if using a conductor with the lowest ampacity possible that can handle the load. So if I calculate, for example, 30 A from UL 508A 32.3.1 and 34.5 A from NEC 215.3, I have a contradiction: UL 508A is telling me to not exceed 30A, while NEC is telling me not to go lower than 34.5 A, so one method results in a 30 A circuit breaker and the other results in a 40 A circuit breaker.
Am I missing something here? I found a question similar to this on this forum a couple years back, but the answers didn't provide any clarification for me. Any help would be greatly appreciated, thanks for bearing with me as I try to understand a completely new field of knowledge.