NEC 220.53 Application Questions
Sparky2791
Northeast, PA
Electrical Design
Hello - I posted these questions in a previous post with other questions but no one replied to them so I am posting it individually.
Question #1
Looking at 220.53. Individual fasted in place appliances, do Electric Water heaters apply to this?
Question #2
Is a microwave considered fastened in place if located above the range but if just sitting on the kitchen countertop it is not?
I ask because if I have a dishwasher a microwave and an electric water heater (if this applies) I need to take the load at 100% of all 3 for the final calculations. If I add a garbage disposal to the total I can use the 75% demand factor for all 4. It would be to your benefit to add the 4th appliance in your calcs depending on the load you use for the 4th appliance it can benefit the over all final load.
There are obviously many scenarios in with this that could apply here is one where it is to your benefit.
20 apartments
3 appliances @ 1kVA each = 60kVA @ 100%
Add a 4th @ .5 kVA
1 appliance @ .5kVA each = 10kVA
60+10 = 70 x .75 = 52.5kVA
Thanks for your replies
Question #1
yes
Question #2
no
your welcome