NEC 220.84 multifamily load calculation

Status
Not open for further replies.

olc

Senior Member
The optional 220.84 calculation for multi-family typically works out significantly less than the regular calculation.
Any hesitation to use the lower number? (which ever is lower)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I assume you realize that there must be electric cooking appliances or use 8kw if it doesn't have electric cooking, to be able to use 220.84
 

crtemp

Senior Member
Location
Wa state
I have a question on this topic too. If I am doing a calc on a 5 unit townhome that has gas ranges and gas furnaces, I can still use Table 220.84 as long as I include a electric range load? So if I include 8kw per unit I would add a total of 18kw (40kw x 45%) per table 220.55?
 