Help me to understand the 2020 NEC 225.30.
I have a detached garage with an existing subpanel fed by a 2 pole 30z
Customer wants a ev charger 50 or 60 amp. Normally I would say refeed the subpanel and feed the charger out of that.
But does the 2020 allow me to feed the garage with 2 circuits as long as they come out of the same panel and. The breakers are side by side.
I don’t have a 2020 in front of me but I think it says they must be grouped together in the separate structure or terminate at one device.
Probably moot anyway, we are technically under the ‘17 and it’s not allowed under that code but I thought about asking for an exception.