Nec 2014 article 230.2 exception for capacity requirement says if exceeds or equal 2000a for 600v or less i am allowed new service. So if i have 208/120 V 800 amps three phase and am adding 1600a 480/277v three phase the 230.2 capacity exception applies?
 

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
Nec 2014 article 230.2 exception for capacity requirement says if exceeds or equal 2000a for 600v or less i am allowed new service. So if i have 208/120 V 800 amps three phase and am adding 1600a 480/277v three phase the 230.2 capacity exception applies?

I think that you can have two services on the building because of different voltages per 230.2(D)
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
So when does capacity requirement come into play? Its says 600V or less. If on the other hand I had 208V/120V three phase 800 amps and am adding new service 1600 amps 208/120V three meet capacity exception?

.
I think that you can have two services on the building because of different voltages per 230.2(D)

Sent from my SM-G935U using Tapatalk
 
Last edited:

packersparky

Senior Member
Location
Wisconsin
Occupation
Inspector
So when does capacity requirement come into play? Its says 600V or less. If on the other hand I had 208V/120V three phase 800 amps and am adding new service 1600 amps 208/120V three meet capacity exception?

.

Sent from my SM-G935U using Tapatalk

Yes. An additional service would be allowed if the total of the 2 services is more than 2000 amps.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Yes. An additional service would be allowed if the total of the 2 services is more than 2000 amps.
So if I have 208/120V, 3 phase, 800 amps service and adding new 208/120V, 3 phase, 1600 amps then that would qualify under capcity exception since they total more than 2000a.

However, if I have 208/120V, 3 phase, 800 amps service and adding new 277/480V, 3 phase, 1600 amps would not qualify under 2000a capacity exception even though two services total more than 2000a?

Sent from my SM-G935U using Tapatalk
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
(D) states that if you have two services with different characteristics they shall be permitted and the 2000 amps thing does not apply.

I. General
230.2 Number of Services. A building or other structure
served shall be supplied by only one service unless permit-
ted in 230.2(A) through (D).
(D) Different Characteristics. Additional services shall
be permitted for different voltages, frequencies, or phases,
or for different uses, such as for different rate schedules
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
I really never understood why this is even in the code. This is really an utility issue and not a code issue.
 

kwired

Electron manager
Location
NE Nebraska
If your utility won't install over certain capacity (usually happens with single phase and not three phase) in one service, then you are allowed multiple services for that situation also.
 