NEC article 230.3 states that service conductors supplying a building or other structure shall not pass thru the interior of another building or structure.
I know the NEC definition of a structure is pretty vague, but can you route a service feeder from the outdoor substation, through a building, and then down into a lineup of outdoor NEMA 3R switchgear?
I know the big reason for this article is likely to guard against penetrating building fire walls, but is this still the case if going thru a standalone building to a piece of gear that is outside?
Thanks
I know the NEC definition of a structure is pretty vague, but can you route a service feeder from the outdoor substation, through a building, and then down into a lineup of outdoor NEMA 3R switchgear?
I know the big reason for this article is likely to guard against penetrating building fire walls, but is this still the case if going thru a standalone building to a piece of gear that is outside?
Thanks