taschendoerfler
- Seattle, WA, USA
230.40 Only one set of service entrance conductors per service drop.
Exception No. 3: A single-family dwelling unit and itsaccessory structures shall be permitted to have one set ofservice-entrance conductors run to each from a single servicedrop, set of overhead service conductors, set of undergroundservice conductors, or service lateral.
Can someone explain the rational for this exception. Why is it allowable, but only for single-family dwelling unit with accessory structures ?
For me this exception seems to potentially create conditions similar to a situation where one doesn't run a dedicated Equipment Grounding Conductor (EGC) from a single service entrance panel to every accessory structure.
Basically, now one has multiple points in the overall system, where EGC and Neutral are bonded (i.e., the various service panels at the accessory buildings). If any water pipes run between the buildings, a parallel low-impedance path back to the source exists.
What if only plastic water pipes are used ? I feel the danger here is that 30 years later during a new project a metal pipe connection is suddenly established and with that a potentially dangerous situation.