I have an apartment building (80 dwelling units total) with three separate meter banks with the following loads calculated for the number of dwelling units on each one under table 220.32. Service is 208 3-phase to 208 single phase meter banks.
Meter bank 1 = 1,167,516 VA X .33 (table 220.32, 30 units) = 385,280 VA = 1069 A
Meter bank 2 = 1,177,533 VA X .33 (table 220.32, 30 units) = 388,602 VA = 1079 A
Meter bank 3 = 812,284 VA X .38 (table 220.32, 20 units) = 308,668 VA = 857 A
Meter bank 1 needs 1200A breaker in switchboard.
Meter bank 2 needs 1200A breaker in switchboard.
Meter bank 3 needs 1000A breaker in switchboard.
Now, can I take the three total loads (before table 220.32 demand) which would be 3,157,333 VA and apply .23 demand factor from table 220.32 for 67+ units and get a total load for bus of 2016 A? In this case I'll have 3 breakers with a total rating of 3400 A on a 2500 A rate bus? Which I believe is ok in accordance with 230.90 exception no. 3.
Or do I have to add the 1069 A, 1079 A, and 857A = 3005 A for the bus rating of the switchboard?
Meter bank 1 = 1,167,516 VA X .33 (table 220.32, 30 units) = 385,280 VA = 1069 A
Meter bank 2 = 1,177,533 VA X .33 (table 220.32, 30 units) = 388,602 VA = 1079 A
Meter bank 3 = 812,284 VA X .38 (table 220.32, 20 units) = 308,668 VA = 857 A
Meter bank 1 needs 1200A breaker in switchboard.
Meter bank 2 needs 1200A breaker in switchboard.
Meter bank 3 needs 1000A breaker in switchboard.
Now, can I take the three total loads (before table 220.32 demand) which would be 3,157,333 VA and apply .23 demand factor from table 220.32 for 67+ units and get a total load for bus of 2016 A? In this case I'll have 3 breakers with a total rating of 3400 A on a 2500 A rate bus? Which I believe is ok in accordance with 230.90 exception no. 3.
Or do I have to add the 1069 A, 1079 A, and 857A = 3005 A for the bus rating of the switchboard?
Last edited: