erickench
Senior Member
- Location
- Brooklyn, NY
Hi Guys, I just need a clarification on the above NEC section. When they speak of ground fault protection do they mean the Phase Overcurrent ANSI #50/51 relays or is it something else?
230.95 does not specify the type of GFP to be utilized but rather stipulates the performance characteristics of the system that is (to be) employed.Hi Guys, I just need a clarification on the above NEC section. When they speak of ground fault protection do they mean the Phase Overcurrent ANSI #50/51 relays or is it something else?
It is not.
If it is medium or high voltage, they mean relay protection with a N or G in the ANSI number.
The code does not require ground fault protection for that system.Okay, N and G mean neutral and ground respectively. I'm designing a 1000A service at 208/120 volts. I'm trying to come up with GFP scheme as per code requirements....