Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
240.15 B says circuit breakers must open all ungrounded conductors both manually and automatically, unless permitted in B1, B2, b3, b4
B2 says single pole breakers can serve multi wire branch circuits for line to neutral loads if the breakers have identified handle ties.
However if the ring or tie is available but not installed they still serve as single pole breakers.
Nec does not say the handle ties must be mechanically connected so why require special breakers at all?
if the intent is to disconnect all ungrounded conductors then why not just us 2 pole breakers?
2 same for single phase circuits line to line loads
3 same for 3 and 2 phase systems with ground
B2 says single pole breakers can serve multi wire branch circuits for line to neutral loads if the breakers have identified handle ties.
However if the ring or tie is available but not installed they still serve as single pole breakers.
Nec does not say the handle ties must be mechanically connected so why require special breakers at all?
if the intent is to disconnect all ungrounded conductors then why not just us 2 pole breakers?
2 same for single phase circuits line to line loads
3 same for 3 and 2 phase systems with ground