I am working on a project where the main distribution board is 65K AIC rated and feeds a 200HP motor(240FLA), a 250HP motor(302FLA)AND MCC Section the has 437FLA worth of motor load. VFD contollers are used for the 2 large motors, the controllers are fed from the main distribution board and are only 18K AIC rated. The Available fault current at the VFD is 23K amps.
240.86(B): Series rating shall not be used where motors are connected on the load side of the higher rated overcurrent device and on the line side of the lower-rated device, and the sum of motor full-load currents exceeds 1% of the interrupting of the lower-rated circuit breaker.
As far as I can tell, series rating can not be used to valadate the 18K AIC VFD. The VFD must be replaced with a VFD that is fully rated(Min 23K). I need some conformation that I am reading the code correctly before I give the owner a heart attack with this information. Can any one out there provide this conformation?
240.86(B): Series rating shall not be used where motors are connected on the load side of the higher rated overcurrent device and on the line side of the lower-rated device, and the sum of motor full-load currents exceeds 1% of the interrupting of the lower-rated circuit breaker.
As far as I can tell, series rating can not be used to valadate the 18K AIC VFD. The VFD must be replaced with a VFD that is fully rated(Min 23K). I need some conformation that I am reading the code correctly before I give the owner a heart attack with this information. Can any one out there provide this conformation?