Re: NEC 240.86 Series Ratings?
All,
I got with the local utility and found that the available fault current on the primary side of the service transformer was 1,300 amps at 14.4KV.
That put my available on the secondary side(not including motor contribution) at 17,400AMPS.
Considering 4,000 amps of motor contribution and routing the feeder to the VFD so it's length was extended to 50LF I was able to get the available fault current at the VFD below the VFD's rating of 18,000 AMPS.
Thanks to all for the input. It certainly provided the best solution for my clients issues.