My situation is this- A 277/480 volt SES feeds a transformer (277/480 to 120/208) within the same building (for a typical tenant suite). The transformer constitutes a separately derived system (no grounded conductor pulled from the SES). The electrician wants to use the equipment grounding conductor from the SES to the transformer to also serve as the transformer's grounding electrode conductor. I'm use to seeing a ground rod driven at the transformer, or attachment of the GEC to building steel at the transformer. Is the electrician's method acceptable?
Thank you- Paul.