NEC 250.50

Status
Not open for further replies.

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
250.50 states all electrodes must be bonded at each building or structure served. Is this only applicable to the GEC at a service entrance, ie, structure “served”?


Sent from my iPhone using Tapatalk
 

Isaiah

Senior Member
Location
Baton Rouge
Occupation
Electrical Inspector
The requirement would include separate buildings supplied by a feeder

The E&C firm wants to bond every foundation in the entire plant to their buried 4/0 copper loop which is buried 18” deep and is very extensive


Sent from my iPhone using Tapatalk
 
Status
Not open for further replies.
Top