i need to extend the end of a branch circuit (single phase 50a 240v residential). the run is about 100ft and buried 20" below grade in plastic conduit. its two 6awg and two 8awg wires, need to go another ~15ft. the termination is a small distribution box (one 50a gfi and two 20a gfi's). this is all outside.
but where in 300.5 does it say i can splice?
edit, i suspect i cant........ i guess they mean like a wire that is rated "UF" or the like and is not in conduit/raceway...... is this correct? if this is the case do i have any options w/o pulling new wire? i cant add a box because it wont be accessible.
if buried conductors in conduit get damaged for any reason, can the damaged section be repaired or does NEC force a re-pull of all the wires?
NEC Article 300.13 requires mechanical and electrical continuity for conductors in raceways. In other words, you cannot have a splice in a raceway (but you can have it in a box or conduit body that has an accessible cover). NEC Article 300.5 does allow splices in direct-buried conductors. That?s because you can use instruments to locate the splices and you can excavate to get to them. However, it?s much more difficult to do maintenance and inspection on conductors that are in raceways.
but where in 300.5 does it say i can splice?
edit, i suspect i cant........ i guess they mean like a wire that is rated "UF" or the like and is not in conduit/raceway...... is this correct? if this is the case do i have any options w/o pulling new wire? i cant add a box because it wont be accessible.
if buried conductors in conduit get damaged for any reason, can the damaged section be repaired or does NEC force a re-pull of all the wires?