What loads are considered diversified loads regarding NEC 310.15(B)(2)FPN #1?How & when is this applied to table B 310.11 in Annex B.
charlie b said:So to say that some conductors will not be carrying current, at least not at the same time as the others, requires you to have some type of interlock or lockout feature included in the design.
The article in question is in the Annex, so there are no ?requirements? at all. But ?load diversity,? as that term is used in B310-11, means that not all the conductors in the raceway will be carrying current at the same time. I submit that absent a physical control, such as an interlock, ?load diversity? cannot be achieved. It is a simple matter of, if current can flow in a wire, it must be counted as a current-carrying conductor.iwire said:I agree it's good design and usually easily accomplished but I don't see a requirement that says they must be interlocked.
How, then, do you determine whether a system has ?load diversity?? Also, what value do you use for the ?Adjustment Factor? for, let us say, 25 conductors in a raceway?iwire said:FWIW here in MA local amendment we use Table B310-11 in place of Table 310.15(B)(2).
charlie b said:How, then, do you determine whether a system has ?load diversity??
FPN: Overheating may occur where continuous, fully loaded conductor diversity is less than 50 percent and the number of current-carrying conductors exceeds nine. See 310.10
Also, what value do you use for the ?Adjustment Factor? for, let us say, 25 conductors in a raceway?