According to 310.3 C,
conductors 8 AWG or larger that are in a raceway, must be stranded
According to 250.64 B 2
A 6 Awg or larger grounding electrode conductor exposed to physical damage musy be protected in (conduit) RMC, IMC, SCH 80 PVC...etc
Likewise, 250.64 B 3
All grounding electrode conductors smaller than 6 AWG must be inztalled in (conduit), RMC, IMC, SCH 80 PBC, etc
However, rarely do i see grounding electrode conductors that are both 8 AWG or larger and installed in raceway to be stranded, yet they pass inspection.
Is this a code that is standard to be overlooked?