NEC 314.16 B1 box fill

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
To make sure I’m doing this right my metal single gang box measures 4”tall x 2/1/8” wide x 1/3/4” deep but NEC book only has similar box at 1/7/8” deep so I chose this?

Book gives total available volume of 13.0” for above box

Therefore the reason 4 x 12 AWG conductors
4 x 2.25 allowance At 9.0” take up

Plus 4 of 12 AWG ground conductors at 1 x 2.25 allowance at 2.25 take up

Plus 1 yoke receptacle under 2”wide is allowance at 2 x 2.25 take up

Added = 15.25 required allowance for a box labeled 13.0 total allowance is reason I can’t get receptacle and wires to fit



However the book does not mention allowance for internal pigtails such as if I were connecting 2 yokes together through the second receptacle pigtailed to the first receptacle in a two gang box

All the book says is give allowance for wires entering, entering and exiting without splice, if looped beyond minimum 6”? Conductor length from entering box point

What do you measure for pigtails for double gang metal boxes?
 

Attachments

  • 0813852E-99BD-4DA3-9F54-CADCEDF7C976.jpeg
    0813852E-99BD-4DA3-9F54-CADCEDF7C976.jpeg
    78.6 KB · Views: 10

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Double gang to be internal pigtail jumped from first receptacle to second receptacle where it is power fed

NEC does not specify allowance for jumpers
 

Attachments

  • FDEECCCA-BEBB-4DF0-A78E-05A8636E9E4A.jpeg
    FDEECCCA-BEBB-4DF0-A78E-05A8636E9E4A.jpeg
    50.6 KB · Views: 7

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
Also in NEC chart what is meant from device vs box for description as I don’t see single gang other than masonry gang?
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
To make sure I’m doing this right my metal single gang box measures 4”tall x 2/1/8” wide x 1/3/4” deep but NEC book only has similar box at 1/7/8” deep so I chose this?

Book gives total available volume of 13.0” for above box

Therefore the reason 4 x 12 AWG conductors
4 x 2.25 allowance At 9.0” take up

Plus 4 of 12 AWG ground conductors at 1 x 2.25 allowance at 2.25 take up

Plus 1 yoke receptacle under 2”wide is allowance at 2 x 2.25 take up

Added = 15.25 required allowance for a box labeled 13.0 total allowance is reason I can’t get receptacle and wires to fit



However the book does not mention allowance for internal pigtails such as if I were connecting 2 yokes together through the second receptacle pigtailed to the first receptacle in a two gang box

All the book says is give allowance for wires entering, entering and exiting without splice, if looped beyond minimum 6”? Conductor length from entering box point

What do you measure for pigtails for double gang metal boxes?
314.16(B)(1) .... A conductor, no part of which leaves the box, shall not be counted.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Also in NEC chart what is meant from device vs box for description as I don’t see single gang other than masonry gang?
A device box is commonly called a gem box, they come in single gang and can be ganged together to form a multi-gang box. For the square boxes (post #2) the cu in measurement is for the box with a blank cover and without an external mud ring or extension box.
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
314.16(B)(1) .... A conductor, no part of which leaves the box, shall not be counted.
A jumper or “pigtail?” Between receptacles, does NOT leave the box nor does it enter or exit the box but is simply made inside the box so I have yet to see what NEC says about the allowance for this as many jumpers can be made within
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
A jumper or “pigtail?” Between receptacles, does NOT leave the box nor does it enter or exit the box but is simply made inside the box so I have yet to see what NEC says about the allowance for this as many jumpers can be made within
Jumpers don't leave the box so they don't count.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
You don't count all the grounds (EGC), just one. Well I understand they changed that some, I don't have that code. Even with the change, you don't count all the EGCs.
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
You don't count all the grounds (EGC), just one. Well I understand they changed that some, I don't have that code. Even with the change, you don't count all the EGCs.
I only counted grounds once for 4 grounds based on largest conductor and table
 