Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
To make sure I’m doing this right my metal single gang box measures 4”tall x 2/1/8” wide x 1/3/4” deep but NEC book only has similar box at 1/7/8” deep so I chose this?
Book gives total available volume of 13.0” for above box
Therefore the reason 4 x 12 AWG conductors
4 x 2.25 allowance At 9.0” take up
Plus 4 of 12 AWG ground conductors at 1 x 2.25 allowance at 2.25 take up
Plus 1 yoke receptacle under 2”wide is allowance at 2 x 2.25 take up
Added = 15.25 required allowance for a box labeled 13.0 total allowance is reason I can’t get receptacle and wires to fit
However the book does not mention allowance for internal pigtails such as if I were connecting 2 yokes together through the second receptacle pigtailed to the first receptacle in a two gang box
All the book says is give allowance for wires entering, entering and exiting without splice, if looped beyond minimum 6”? Conductor length from entering box point
What do you measure for pigtails for double gang metal boxes?
Book gives total available volume of 13.0” for above box
Therefore the reason 4 x 12 AWG conductors
4 x 2.25 allowance At 9.0” take up
Plus 4 of 12 AWG ground conductors at 1 x 2.25 allowance at 2.25 take up
Plus 1 yoke receptacle under 2”wide is allowance at 2 x 2.25 take up
Added = 15.25 required allowance for a box labeled 13.0 total allowance is reason I can’t get receptacle and wires to fit
However the book does not mention allowance for internal pigtails such as if I were connecting 2 yokes together through the second receptacle pigtailed to the first receptacle in a two gang box
All the book says is give allowance for wires entering, entering and exiting without splice, if looped beyond minimum 6”? Conductor length from entering box point
What do you measure for pigtails for double gang metal boxes?