I’m kind of confused here. Normally you size the junction box at 6 times the conduit trade size and add the sum of those below for angled runs or size the box to 8 times the conduit trade size for straight pulls
However I am installing a plastic junction box where # 4 AWG SOOW Cord will be entering from the bottom splicing inside and exiting adjacent to the first at the bottom for a u bend
The cable entering is not a conduit so would I base the size of the junction box based on the size of any conduit that if installed would hold the SOOW cord or 4 of #4 AWG conductors?
Or #4 AWG x 6 = 24 inch box is obviously not right because the jacketed SOOW Cord is not a conduit?