I was recently asked whether nonmetallic boxes are allowed for receptacle installations. Obviously they are in homes, but what about in commercial settings? Certain medical imaging rooms do not allow ferrous materials and so we wanted to install PVC boxes with PVC conduit going to them.
314.3 seems to allow nonmetallic boxes as long as nonmetallic raceways are used. Is the installation allowed if we use PVC conduit?
An electrical inspector questioned whether this would work due to grounding concerns. I am not really sure what he meant as I don't think the PVC box needs to be grounded. We are providing an equipment grounding conductor for the outlet and therefore the component that plugs into the outlet will be grounded as well.
314.3 seems to allow nonmetallic boxes as long as nonmetallic raceways are used. Is the installation allowed if we use PVC conduit?
An electrical inspector questioned whether this would work due to grounding concerns. I am not really sure what he meant as I don't think the PVC box needs to be grounded. We are providing an equipment grounding conductor for the outlet and therefore the component that plugs into the outlet will be grounded as well.