Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
Yes i understand what the NECs intent was most likely such as avoiding sharp nails for covers to penetrate wiring inside cabinets. Thus screw length limits were provided for covers but this does not exclude nails that "enter wiring space" for cabinet securement.That enter wiring spaces , they are taking about screws you use to secure covers , like a 4” metal 1900 box blank cover , the 8-32’s will enter the wiring space so they have to be blunt ends , in no way does the language adress what you are saying, how can you consider the end of a screw you use to rigidly secure a box to a surface as entering the wiring space ?? It may enter for 1/2 a second when you secure the box but that’s not what the language or intent is adressing and the code making panels expect us in the field to actually have common sense and common sense says this rule has nothing to do with the point of the screw used to secure the box to a surface . If it did how would it be code compliant to mount regular 4” 1900 boxes to a surface unless they were bracketed ?? Think about it
Although i would not recommend nailing mounting screws after wiring installation it can and will be done