I may have discovered another oddity in the NEC. The above section states:
"FMC less than 1/2" shall not be used unless permitted in 348.20 (A) (1) through (A) (5) for trade size 3/8"
Now I have searched the internet and I have'nt been able to find 1/4" flexible metal conduit. So I guess this rule is meant to forbid it's use. But if the rules for
3/8" conduit are layed out in (A) (1) through (A) (5) then should'nt these same rules apply to either 1/2" or 3/4" FMC as well? Again these rules should apply to either the larger or the smaller of the two. Also, the language is'nt appropriate. It should just read:
"FMC less than 1/2" shall not be used".
And then indicate whether rules (A) (1) through (A) (5) apply to FMC larger or smaller than 3/8".
"FMC less than 1/2" shall not be used unless permitted in 348.20 (A) (1) through (A) (5) for trade size 3/8"
Now I have searched the internet and I have'nt been able to find 1/4" flexible metal conduit. So I guess this rule is meant to forbid it's use. But if the rules for
3/8" conduit are layed out in (A) (1) through (A) (5) then should'nt these same rules apply to either 1/2" or 3/4" FMC as well? Again these rules should apply to either the larger or the smaller of the two. Also, the language is'nt appropriate. It should just read:
"FMC less than 1/2" shall not be used".
And then indicate whether rules (A) (1) through (A) (5) apply to FMC larger or smaller than 3/8".