I have read through several threads dealing with flexible power cords and suspended ceilings. In the AV business the method of mounting a projector from the ceiling, routing the flexible power cord through the mounting pipe, and attaching the plug to a receptacle mounted above the ceiling is VERY common for non plenum situations. As shown below:
The common rule simply is: no outlets above plenum ceilings, but non plenum is OK.
This seems to be unresolved. Some of my colleagues suggest 400.7(8) allows us power a projector in this fashion. It has been done a thousand times over without the rebuttal of an inspector. Others (like Pierre) does not agree. I also liked Roger's point from another thread:
The AV industry has produced several UL listed solutions to allow integrators to use this method in plenum situations. For example, this product from Chief Manufacturing:
http://www.chiefmfg.com/productdetail.aspx?AccessoryID=208
This box is mounted above the ceiling inline with the pipe that the projector mounts to. The installer routes the cabling through the mounting pipe and into the box where it plugs into an outlet mounted on the inside of the box. This allows for the flex plug to be connected to an outlet above the ceiling without being exposed to the plenum space. This box is UL listed.
So: If 400.7(8) does not allow me to power a projector from above a lay-in tile ceiling then this box by Chief also violates 400.8(5) and (6); but UL approved this box and the function it serves.
Thoughts?
Pierre C Belarge said:Here is an example of how receptacles for projectors are sometimes installed
![]()
And the receptacle -NICE
![]()
The common rule simply is: no outlets above plenum ceilings, but non plenum is OK.
This seems to be unresolved. Some of my colleagues suggest 400.7(8) allows us power a projector in this fashion. It has been done a thousand times over without the rebuttal of an inspector. Others (like Pierre) does not agree. I also liked Roger's point from another thread:
....this made me laugh.Roger said:'Since "Pendants" are specifically permitted to be connected by flexible cord, 400.7(A)(1), you say it is legal to run this cord strapped to a structural ceiling, through a door way, then strap it to a wall for say 10 feet, then through a hole in the wall, then strap it up a wall to a suspended ceiling, then through a hole in this suspended ceiling to a receptacle located above the ceiling, is this correct?'
The AV industry has produced several UL listed solutions to allow integrators to use this method in plenum situations. For example, this product from Chief Manufacturing:
http://www.chiefmfg.com/productdetail.aspx?AccessoryID=208
This box is mounted above the ceiling inline with the pipe that the projector mounts to. The installer routes the cabling through the mounting pipe and into the box where it plugs into an outlet mounted on the inside of the box. This allows for the flex plug to be connected to an outlet above the ceiling without being exposed to the plenum space. This box is UL listed.
So: If 400.7(8) does not allow me to power a projector from above a lay-in tile ceiling then this box by Chief also violates 400.8(5) and (6); but UL approved this box and the function it serves.
Thoughts?