Gaffen99
Senior Member
- Location
- new jersey
Clip the tabs on the outlet to render the lower part useless....Pointless?....
You can file a complaint against this unprofessinal Electricial inspecter.http://www.mass.gov/Eoca/docs/dpl/complaint.pdfAny input would be greatly appreciated. Regarding 422.12 - we are wiring furnaces and we are using the existing dedicated circuit from the old furnace in residential apartments. there is a condensate pump being installed that plugs in. according to 422.12 exception #1 we can install a receptacle tapped off the same circuit as the furnace for the condensate pump that plugs in. (we installed a duplex receptacle next to the service switch - in a utility closet not requiring gfci protection)
The question is - does this have to be a single receptacle or is a duplex receptacle a legal installation? I have an inspector telling me that I have to install a single receptacle because there will be a receptacle not in use which makes the circuit not dedicated. Further more - in a basement I would have to use a duplex gfci receptacle because I don't think a single gfci receptacle exists.
I think he is over reading into the actual intent of this code. He claims that leaving an open receptacle - someone could come along and plug something else into it. well, you could simply unplug the condensate pump and plug anything into that as well.
It is my opinion that the code does not address this issue therefore it is a legal installation.
He then told me to cut off the plug on the condensate pump and hard wire it or put silicon over the unused receptacle so no one could use it. I think both of those suggestions void the ul listing of those products.
If I installed a sticky label that read "receptacles for heating equipment only" would that then satisfy anything?
I'm just curious, since the 2008 has removed all exceptions to having a dedicated receptacle in a basement from not being GFCI protected, how would you get by this?
Putting in a single receptacle to prevent plugging other items into the circuit does not work. I have seen many triple taps, power bars, etc. plugged into single receptacles that were intended for a single utilization equipment. At the very least you should put another receptacle nearby so they hopefully use it instead.I have also seen condensate pumps with cord cap removed and wired into furnace. This is not a NEC compliant way to connect them. For those who are afraid of the unit being unplugged or a GFCI tripping and having the condensate flood the area, every one of these pumps comes with a limit switch to shut down the HVAC equipment if the resevoir is full, but I never see it connected. That is what the two wires sticking out of the unit are for.
Who said it is an unfinished basement?
Usually apt. furnaces are in a closet in the hallway.I presume the receptacle in question is in the mechanical room/space. 210.8(A)(5) defines what it means by unfinished basement and this space seems to fit the definition whether the rest of the basement is finished or not.
Didn't catch that in the OP:roll:, just was responding to what others said about using a single receptacle instead of a GFCI.Who said it is an unfinished basement?
I presume the receptacle in question is in the mechanical room/space. 210.8(A)(5) defines what it means by unfinished basement and this space seems to fit the definition whether the rest of the basement is finished or not.
residential apartments
[/U]
Usually apt. furnaces are in a closet in the hallway.
Any input would be greatly appreciated. Regarding 422.12 - we are wiring furnaces and we are using the existing dedicated circuit from the old furnace in residential apartments. there is a condensate pump being installed that plugs in. according to 422.12 exception #1 we can install a receptacle tapped off the same circuit as the furnace for the condensate pump that plugs in. (we installed a duplex receptacle next to the service switch - in a utility closet not requiring gfci protection)
The question is - does this have to be a single receptacle or is a duplex receptacle a legal installation? I have an inspector telling me that I have to install a single receptacle because there will be a receptacle not in use which makes the circuit not dedicated. Further more - in a basement I would have to use a duplex gfci receptacle because I don't think a single gfci receptacle exists.
I think he is over reading into the actual intent of this code. He claims that leaving an open receptacle - someone could come along and plug something else into it. well, you could simply unplug the condensate pump and plug anything into that as well.
It is my opinion that the code does not address this issue therefore it is a legal installation.
He then told me to cut off the plug on the condensate pump and hard wire it or put silicon over the unused receptacle so no one could use it. I think both of those suggestions void the ul listing of those products.
If I installed a sticky label that read "receptacles for heating equipment only" would that then satisfy anything?
Only if it is at or below grade see 210.8(A)(2)
there are no tabs to break on a gfci receptacle. Gun away I say - he is no better than you or me. He has to live by the same code book we live by.
right is right - wrong is wrong. why should we have to tolerate nonsense?
Most all the inspectors I have ever dealt with are great and very knowledgeable. I call a few of them all the time and bounce questions off them - even if it isn't a job in their town or city. They are happy to help.
I'm not convinced he's wrong. Not that it matters.![]()
I'm not convinced he's wrong. Not that it matters.![]()
the inspector cited 422.12 and article 100 definition of "individual branch circuit" as the basis for saying that the duplex receptacle is against code.
Branch Circuit, Individual. A branch circuit that supplies
only one utilization equipment.