I'm working on coordinating some motor protection. I am familiar with the differences between an Instantaneous Trip breaker (a motor circuit protector--can only be used in a listed combination starter with overloads) and an Inverse Time breaker. I have read the details and exceptions listed in the NEC 2005 Article 430. What I haven't found in the code is a combination thermal-magnetic breaker with an adjustable instantaneous trip. Most inverse time (thermal) breakers have a fixed instantaneous, but a GE TKMA for example has an adjustable instantaneous trip.
My thought, and please tell me if I've missed something, is that you use both columns for the appropriate segments.
Example: 250HP induction motor on 480V. Using Table 430.250, the full load current is 302. 250% of that is 755A, so my 500A GE TKMA is well within the limits. 800% of the FLC is 2416A, and so an instantaneous setting of 5000A (the max for this breaker) is too high, but a setting of 2250A is acceptable.
Is there anything I'm missing, or is this interpolation correct?
My thought, and please tell me if I've missed something, is that you use both columns for the appropriate segments.
Example: 250HP induction motor on 480V. Using Table 430.250, the full load current is 302. 250% of that is 755A, so my 500A GE TKMA is well within the limits. 800% of the FLC is 2416A, and so an instantaneous setting of 5000A (the max for this breaker) is too high, but a setting of 2250A is acceptable.
Is there anything I'm missing, or is this interpolation correct?