Hello everyone:
I'm not sure if I'm quite sure I do understand this article (513.3 B):
(B) Areas Not Cut Off or Ventilated. The entire area of
the hangar, including any adjacent and communicating areas
not suitably cut off from the hangar, shall be classified as a
Class I, Division 2 or Zone 2 location up to a level 450 mm
(18 in.) above the floor.
If I have an adjacent area to the hangar and separated by a door. The hangar space is ventilated (exhaust ducts located at 1'-0" above finished floor) . Does the areas adjacent to the hangar (example: Corridor or any rooms) with direct doors to the hangar space consider to be unclassified areas?
Thanks,