We have a renovation project in a doctor's office. The scope of work is to add an additional receptacle to the existing exam rooms.
The electrical contractor used healthcare rated MC cable (HCF-MC) for the new devices but the existing installation has regular MC cable (not health care rated). Both the existing and new MC cable have an insulated equipment grounding conductor so i don't think there is an issue with NEC 517.13(B) since this is continuous back to the panel. However, the existing MC cable armor is not listed as an equipment grounding conductor so the electrical contractor connected the new MC cable armor to the existing MC cable equipment grounding conductor. While this would provide an effective ground-fault current path per NEC 517.13(A) I don't think it complies with the intent of a redundant ground path. Is this a code violation?
Can the contractor connect the new MC cable armor to a new (separate) equipment grounding conductor back to the panel ran outside of the existing MC cable? They are trying not to replace all the existing wiring with new HCF-MC.