Hi all,
Designing a backup system for a small clinic. I've got a type 2 EES with the only life safety equipment being egress lighting and some task lighting. I've got an equipment branch as well.
Going through article 517 it gives guidance on the backup run time requirements for the life safety branch (article 517.26) stating to follow article 700. So I assume 90 minute backup for the life safety branch but what about the equipment branch? Planning on using battery backups for the egress/task lights, and a generator for the equipment branch but I don't see a section that states run time requirements for the equipment branch or that points back to any of the 700, 701 or 702 articles? I looked through a few other NFPA codes, and found most point back to NEC 517. Have you all ever come across this or designed something similar?
Thanks!
Designing a backup system for a small clinic. I've got a type 2 EES with the only life safety equipment being egress lighting and some task lighting. I've got an equipment branch as well.
Going through article 517 it gives guidance on the backup run time requirements for the life safety branch (article 517.26) stating to follow article 700. So I assume 90 minute backup for the life safety branch but what about the equipment branch? Planning on using battery backups for the egress/task lights, and a generator for the equipment branch but I don't see a section that states run time requirements for the equipment branch or that points back to any of the 700, 701 or 702 articles? I looked through a few other NFPA codes, and found most point back to NEC 517. Have you all ever come across this or designed something similar?