In the Middle East we see a mixture of codes in use, but mainly NEC/NFPA and UK (BSI).
Per NEC 517.30.C.3, the emergency system wiring for a HCF shall be mechanically protected.
I understand that typically this constitutes metal conduit but could include concrete-encased schedule 40 PVC piping.
As I'm from the UK my first thought for the MV installation is armoured cable (ie XLPE/SWA) on tray.....
Question.: could the armouring be classed as mechanical protection or should the distribution cabling be installed within a conduit system to meet NEC?
thanks!!