Keep in mind that the exception to 517.13(B) for lights above 7.5 Feet only allows you to eliminate the insulated copper EGC the wiring method itself must still qualify as the EGC so standard MC is not permitted to connect luminaires in patient care areas even if they are 8 feet above the floor.
Chris
Which is what I said in post # 10
Roger
The way I've always seen it interpreted around here is that above 7.5 feet is not considered a "patient care area" and that standard MC
is allowed for lights above 7.5 feet. Since if it is
not a patient care area, 517.13(A) and (B) would not even apply.
The code allows the engineer or facility to deem what is and is not a patient care area, and since the term "patient vicinity" also uses the 7.5 foot limit, I believe that is the reasoning behind allowing it. I'm not sure if this is an official NC Department Of Insurance interpretation, or not.
I have never wired a light above 7.5 feet with HCF, and I probably have done a dozen dentist or doctors offices, just this year alone.
I did get tripped up one time many years ago, not realizing that a dentist lights attached to the ceiling can be extended down well past the 7.5 foot limit, though. :slaphead: