How would you apply this article to an installation in an Industrial application?
Does 590 eliminate the need to follow specific requirements of other code sections.
As the Engineer has saved money and the inspector has approved it who am I to object.
Recently we installed a 400hp 480v 3 PH 60 HZ 700 RPM 498 Amp Motor.
The Feeder for this motor is ground floor, outside the building in Switchgear with a rack in 1000 Amp Frame set to 600A with .7 sec Ground and 1600 Amp Series fuses.
500MCM parallel is used to feed a Softstart three floors down that sits 2 ft from the motor. The 800 hp soft start has electronic OL protection and an on-off pushbutton start in the softstart cabinet.
There are NO fuses in the softstart cabinet. There is no Disconnect Here, all hard wired.
Installation as a temporary could be as long as two years.
There is no Local Disconnect for the controller as per:
430.102 Location.
(A) Controller. An individual disconnecting means shall be provided for each controller and shall disconnect the controller. The disconnecting means shall be located in sight from the controller location.
Can 590 do this else where?
Does 590 eliminate the need to follow specific requirements of other code sections.
As the Engineer has saved money and the inspector has approved it who am I to object.
Recently we installed a 400hp 480v 3 PH 60 HZ 700 RPM 498 Amp Motor.
The Feeder for this motor is ground floor, outside the building in Switchgear with a rack in 1000 Amp Frame set to 600A with .7 sec Ground and 1600 Amp Series fuses.
500MCM parallel is used to feed a Softstart three floors down that sits 2 ft from the motor. The 800 hp soft start has electronic OL protection and an on-off pushbutton start in the softstart cabinet.
There are NO fuses in the softstart cabinet. There is no Disconnect Here, all hard wired.
Installation as a temporary could be as long as two years.
There is no Local Disconnect for the controller as per:
430.102 Location.
(A) Controller. An individual disconnecting means shall be provided for each controller and shall disconnect the controller. The disconnecting means shall be located in sight from the controller location.
Can 590 do this else where?