I look at the above NEC section and I see a contradiction with NEC 680.12 that it references. The last sentence of 600.6 reads thus:
"Signs and outline lighting systems located within fountains shall have the disconnect located in accordance with 680.12."
But the first sentence of NEC 680.12 reads the following:
"One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting."
NEC 680.12 does not pertain to lighting in any way. Of course the last sentence reads:
"Each means shall be readily accessible and within sight from it's equipment."
But again this section was not meant for lighting.
"Signs and outline lighting systems located within fountains shall have the disconnect located in accordance with 680.12."
But the first sentence of NEC 680.12 reads the following:
"One or more means to disconnect all ungrounded conductors shall be provided for all utilization equipment other than lighting."
NEC 680.12 does not pertain to lighting in any way. Of course the last sentence reads:
"Each means shall be readily accessible and within sight from it's equipment."
But again this section was not meant for lighting.