My question pertains to 645.5 (D) (5): According to this section it appears that any cord-and-plug power cables for IT equipment residing under a raised floor used for ventilation is required to be listed as Type DP.
We have a IT equipment vendor claiming his SJTOW power cables ARE plenum rated.
Any recommendations on verifying this? I would have expected to see the "DP" stamped on the cable sheath, like you would see on communications cabling.
We have a IT equipment vendor claiming his SJTOW power cables ARE plenum rated.
Any recommendations on verifying this? I would have expected to see the "DP" stamped on the cable sheath, like you would see on communications cabling.