I am confused about NEC 690 10(E). By definition in 690 .2, a Stand-Alone System is a PV system that supplies power independently of an electrical production and distribution network. NEC 690.10(E) requires breakers to be secured for stand-alone inverters on both stand-alone or utility-interactive systems. Is not a stand-alone inverter, by definition in 690 .2 not a utility-interactive system? Any thoughts?
 

RAYMFL

Senior Member
Location
Seminole Co
Stand alone inverters can also be interactive. In other words, an inverter could operate as an interactive unit or operate as a stand alone unit when there is no utility power available and batteries are used as the source of power.

Ray
 

wyboy

Senior Member
But what makes a stand-alone system a stand-alone system if it is utility-interactive?690.10(E) says, "Back-fed Circuit Breakers. Plug-in type back-fed circuit breakers connected to a stand-alone inverter output in either stand-alone or utility-interactive systems shall be secured in accordance with 408.36(D)." By definition in 690 .2, a Stand-Alone System is a PV system that supplies power independently of an electrical production and distribution network. How can a system or inverter be both stand-alone and interactive at the same time?
 

dana1028

Senior Member
But what makes a stand-alone system a stand-alone system if it is utility-interactive?690.10(E) says, "Back-fed Circuit Breakers. Plug-in type back-fed circuit breakers connected to a stand-alone inverter output in either stand-alone or utility-interactive systems shall be secured in accordance with 408.36(D)." By definition in 690 .2, a Stand-Alone System is a PV system that supplies power independently of an electrical production and distribution network. How can a system or inverter be both stand-alone and interactive at the same time?

They are not stand-alone/utility interactive at the same time. This is an interactive system that has the ability to be a stand-alone...i.e. when you lose utility power the system switches over to the stand alone components [battery back up - direct PV usage, etc.].
 

RAYMFL

Senior Member
Location
Seminole Co
If the inverter is only interactive, then 408.36(D) would not apply. The text reads "circuit breakers connected to a stand-alone inverter output". All the stand-alone systems I've had experience with on dwellings have incorporated the capability of being used as interactive when utility power is available. The only truly stand-alones I've seen are for dedicated pieces of equipment like gate operators.